I was recently going to install a Lutron Maestro Occupancy Sensor (MS-OPS2), but I noticed in the installation instructions that it said the device wouldn't work without an equipment grounding conductor connected. This seemed strange to me, so I did a bit of research. I found that the device actually uses the grounding conductor as a grounded conductor, so it can have constant power. It only seems to be a small amount of current, as this document says you should be able to connect 20 devices before tripping a GFCI at 4-6mA.
But why is this allowed at all? Why are devices allowed to intentionally create ground faults? Shouldn't a normally non-current-carrying conductor, normally not carry current?
But why is this allowed at all? Why are devices allowed to intentionally create ground faults? Shouldn't a normally non-current-carrying conductor, normally not carry current?