kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
You would replace all that copper without first checking where those magnetic trip settings should be set to?Fair enough and it is reasons like that we have had a power recording meter on it for some time in the past. Never tripped while it was in place.
Tonight they will be testing the underground run with better methods than we have. It should be interesting.
In most cases we would have simply replaced the conductors at this point but its about 2,000' of I think 500 kcmil, copper for sure and to top it off the a floor standing ATS has to be moved out of the way to do the pull.
We would have a window from 11PM to 6AM to make it happen if that is what need to get done.
If megging those conductors don't indicate a fault, I am not going to jump on the bandwagon of replacing them so quickly. You lose some credibility when you spend that kind of money and yet don't fix anything.