I guess not impossible. I would have to assume Bob has done some investigating of the loads supplied and would have likely found something if that is what is happening, but I have asked if a simple megger test has been done and haven't really gotten an answer either.I'll pose a theory....what if the upstream transformer is an ungrounded "floating" wye providing the 480/277V source. Then if the 70a breaker has a ground fault on say 'A' phase and the 100a breaker has a ground fault on 'B' phase you would have a L-L fault that could cause all three breakers to trip.
As for why it happens when it is wet...maybe one of the ground faults is on a downstream 277V outdoor light fixture that is fed from a contactor. So you wouldn't necessarily see the fault with a megger when deenergized.
Sent from my iPhone using Tapatalk
First post he indicated a basic mega test had been done.I guess not impossible. I would have to assume Bob has done some investigating of the loads supplied and would have likely found something if that is what is happening, but I have asked if a simple megger test has been done and haven't really gotten an answer either.
Megger test is usually prior to commissioning a new install. This is existing installation. A fault could easily be ascertained per my last post.I have asked if a simple megger test has been done and haven't really gotten an answer either.
That was over 60 posts ago and is forgotten by nowFirst post he indicated a basic mega test had been done.
That was over 60 posts ago and is forgotten by now![]()
From what little I have seen and heard, I'd certainly look into those magnetic trip settings before doing much else if it were my job to solve this.
I'd probably do that before hiring a third party to monitor things.
I have never told you where to set them or how to determine their proper setting, I don't really know how to determine where to set them. I did think it looked a little suspicious as soon as I seen they were all at minimum settings and pointed that out, ever since then you seem to have been trying to prove I was wrong about something. Seems logical to me that any high inrush type of load can potentially give trouble with a low magnetic trip setting. Do you want to put line reactors on those circuits to reduce the inrush or do you want to figure out where to set the magnetic trip? Either way will involve some calculating of available current and impedances of circuits and loads.What does that mean look into it? Can you do the calculations?
I sometimes really question if you read what has been posted.:huh:
No one is getting hired to monitor anything.
A company, that specializes in electrical conductor, equipment testing and commissioning was hired to look at the installation and give their professional opinion.
The technician on site took notes, photos, IR images, of many things, including the breaker settings and is going to put all that into a pretty report that will get turned into the customer for their in house engineers to use and base decisions on.
Next week I may well be back there cranking the settings but that will be an engineers call not mine.
This 200 amp breaker that is tripping is only one other 200 amp breaker away from the service disconnect. For all I know raising the mag trip on these breaker could just push faults up to the main. I am not quilfied to determine breaker settings.
Try paying more attention the opening post instead of the side conversations.
- The 70 amp breaker tripped in a span of say 10 to 30 minutes from when we re-energized. None of us where in the area when it tripped.
- It was reset and did not trip again
No one is getting hired to monitor anything.
A company, that specializes in electrical conductor, equipment testing and commissioning was hired to look at the installation and give their professional opinion.
The technician on site took notes, photos, IR images, of many things, including the breaker settings and is going to put all that into a pretty report that will get turned into the customer for their in house engineers to use and base decisions on.
You don't seem impressed by this testing company...
:? Why would you say this? Nothing iwire has said in this thread has given any indication of that.
Since the problem is intermittent, it may be prudent to do some sort of event monitoring. If you already have, please ignore this message.
We put our PQ recording on it for a while, until we needed it for another job.
We did not catch a thing during that time. :weeping:
We put our PQ recording on it for a while, until we needed it for another job.
We did not catch a thing during that time. :weeping:
Does your PQ gear record current? If so, how close to the breaker rating is it? For instance, is it 80% or 20%?