Pg 6-47 https://www.geindustrial.com/catalog/buylog/06_BuyLog2013_MoldedCaseCircBrkrs.pdf
Instant trip setting range min/max ~300/1000%
do these have a thermal/toc element?
Current settings
200 590
100 295
70 ~340
the 70 likely trips on xfmr inrush, set it 9 x xfmr current 500 A, 700%
same for the 200 (plus other loads), set at 600% 1200 A
100, no idea, but setting at 600% or 600 A should be no issue
most i/t molded case don't get to the instant range 1000-1200 %
I understand the thread is long so its easy to overlook some of the comments.
The transformers have never to my knowledge tripped when energized. I have personally energized them without trouble and have watched them be energized without trouble.
The trips have happened well after the circuits were energized.