We call them "NAC panels" here.
NAC one brand calls them SNAC.
We call them "NAC panels" here.
NAC one brand calls them SNAC.
Apparently you have not bothered to look up the actual breaker data sheets yourself.
Magnetic trip only breakers are relatively rare. Magnetic only mounted into standard panelboard construction are extremely rare, and may no longer even exist.
If you use that term in conversation with anyone who is familiar with both fire alarm and sprinkler, I'm betting 99 out of a hundred will assume you mean a notification appliance booster power supply. especially since it says "alarm", and the hundredth will ask you to repeat the question.
Apparently you have not read the thread before commenting...
Pg 6-47 https://www.geindustrial.com/catalog/buylog/06_BuyLog2013_MoldedCaseCircBrkrs.pdf
Instant trip setting range min/max ~300/1000%
do these have a thermal/toc element?
Current settings
200 590
100 295
70 ~340
the 70 likely trips on xfmr inrush, set it 9 x xfmr current 500 A, 700%
same for the 200 (plus other loads), set at 600% 1200 A
100, no idea, but setting at 600% or 600 A should be no issue
most i/t molded case don't get to the instant range 1000-1200 %
disagree
never heard a fa panel referred to as a 'booster' panel (btw, that word is not used in the panel schedules)
been to the following schools: Ansul, Fenwal, Kidde, Pyrotonics, Edwards, Honeywell, etc.
Worked for a firm for 4 years that did a large amount of work with fire/explosion suppression/detection (along with power dist) in the oil fields of Alaska, military facilities, telecomm facilities and Boeing facilities in WA: Seatronics Protection Systems
You probably should drop this and move on. It is not pertinent to the conversation. Furthermore the fact I wrote it gives me 100% confidence it had nothing to do with a motor.
There are no motor loads.
here
I if we're being 100% technically correct let's call it a transient.There is no fault, just a temporary spike in current when that transition is made.
Yes page 6-47 includes the code for the part number.
Did you look at page 6-91?
The letter T, in position #8, indicates the breaker has Long time (e.g. thermal) tripping. There would be a letter I here, if this was a Motor Circuit Protector frame for magnetic only protection.
I if we're being 100% technically correct let's call it a transient.
Just like I noted in post #185.pg 6-47 also shows a note for the T code as LSI an industry std term for LongShortInstant
Actually the pressure maintenance pump can be supplied from the normal service or the fire pump service, but I otherwise agree you almost never hear it called a "fire alarm" anything, maybe a "fire pump" something though.All true, but no one calls the main fire pump or booster fire pump service a "fire alarm booster panel", "FA supply", or "fire alarm control panel". Not to mention they wouldn't be coming out of a distribution panel in any event.
Just like I noted in post #185.
It appears that you heard hoof steps and thought of Zebras instead of horses.
I think it is time to stop digging. and look back to what the OP has posted throughout this thread.
:thumbsup:300% is way too low
the breakers are set correctly and can't be set higher for some reason
I would selectively set breakers higher to identified which branch was the source (main, 70 or 100)
or just set all higher to 800-1000% and call it a day
300% is way too low
So you are good without finding the reason they are tripping and simply cranking up settings.
Duly noted.
Let me say this assumes what is there already is in compliance with the available fault current and AIC ratings as well as any series ratings for downstream devices.If you replaced them with a breaker that didn't have magnetic trip adjustment, chances are the fixed magnetic trip is at least 600 or even 800% of the breaker rating.
I really don't know you can turn them too high from a overcurrent protection perspective, any specific setting you do put them at is for selective coordination purposes - with the intent that the branch breakers will trip before the main does if there is a fault on a branch circuit.
If you turned the main up, I'd bet your random tripping event ends up only tripping the branch breakers.
If you turned up the branch units but not the main, you probably only see the main trip during whatever event is occurring.
How much to turn each one up is for selective coordination, they are still going to protect the wiring from short circuits and ground faults even at maximum settings.