Given that the OP was aware of the unbalance issue I think there was no chance he put all the breakers on one busbar. Seems to me the OP knows about trying to balance the 120 volt loads. I do agree exactly 1/2 might not happen but the OP did say "generally".I just want to point out that the way this OP was phrased, to me, implies somewhat unsound reasoning. The service neutral could theoretically carry as many amps as either of the ungrounded conductors if the load is somehow entirely unbalanced, i.e. all on one of those ungrounded conductors. And I don't believe there is anything special about the 1/2 number; if that number is thought to come from 120/240 that is a false understanding.
I saw a house once where some not-very-bright person put all the branch breakers on one busbar. (The panel was literally half full). Not sure why they did that, but I wouldn't tell that person that the service neutral could be smaller until they demonstrated some improved understanding in other areas. :happyno:
add: and you would have to ignore the 240 volt loads, which is unsound reasoning.