Lets start here
Th above tells us we have to comply with both A & B, not one or the other.
The above lays out what activities this applies to and what sections we have to comply with
That is the very limited exception to the GFCI protection required by section (A).
(A)(1) above applies unless you fit the narrow limitations of the exception above. No assured grounding program allowed for those receptacles.
Now lets move on to (B) where we can find the assured grounding program.
So section (B) does not apply to any 125 volt, 15, 20 and 30 amp receptacles and therefore the assured equipment grounding program cannot be used for those receptacles.
Assured equipment grounding can only be used in place of GFCI for circuits greater than 30 amps and 125 volts.
Sure. That is an instance. But it is not the continuum of what "current leakage from the insulated circuit path" covers. What about all manner of mis-wiring?
What about an open neutral with the live conductor short to EGC connected exposed metal in the hands of a person working on the end of a long small guage branch circuit and extension cord, a person who is exposed to an intimate connection with Earth?
![]()
In this scenario, the GFCI detection is absent, but there is a good EGC. Circuit analysis yields a whooping 56 mA through body "leak".
![]()
I find this conclusion to be a disturbing misdirection.
Load current is intended to stay in an insulated,
and contained, path, from the source, through the load and back to the source. Detection of leakage of current, and the interruption of the leakage current, from that intended path is the purpose of the GFCI. Period.
If code requires it eventually manufactures will make it,d.
More like,,, If code requires it manufactures can sell it.
It is a ton easier to get past the CMPs than it is the UL. It's a loophole that needs to be closed.
I'm hearing the '17 will require GFCI protection for all commercial receptacle outlets 100A and less....
Inasmuch as GFCI protective devices exist for say 100A 3ph, i don't believe there is a 100A 3phgfci breaker on the market....at least not yet
~RJ~
I'd wager it mortality & morbidity MBrooke , it always is
The irony is trying to address all the 3rd world junk we power up...
~RJ~
You're kidding, right?Then why does the code let you get away with an un-insulated service neutral? I know I am nit picking, but technically this statement is not correct.
Again this is a baseless misdirection, in my opinion.Correct. However that fact does not change history.
The open neutral can be anywhere in the branch circuit, extension cords or tool.Open neutral where? At the service? If so a GFCI will not protect you.
That is a total misdirection, as voltage drop does not preclude the presence of current escaping the intended circuit path.But if the above scenario was such a concern, why does the NEC only make recommendations- not mandatory restrictions- on voltage drop?
is countered by my illustrated scenario, as there is an intact EGC present, and the quality of the poor worker's connection to Earth is augmented by water and/or moisture.GFCIs, they were simply- and still are- another type of EGC. They were created and mandated soley to address the issues asociated with missing EGCs. Not water or moisture.
You're kidding, right?
The load side of a class A GFCI is not in the Service Conductors.
Again this is a baseless misdirection, in my opinion.
The "Fact," as I stated it, and as you agreed is "Correct," IS HISTORY. Your own reference to source material about 1962 in this thread says so.
The open neutral can be anywhere in the branch circuit, extension cords or tool.
That is a total misdirection, as voltage drop does not preclude the presence of current escaping the intended circuit path.
Your OP reductionist claim:
is countered by my illustrated scenario, as there is an intact EGC present, and the quality of the poor worker's connection to Earth is augmented by water and/or moisture.
I chose to illustrate a construction power setting, purely for the engineering analysis simplification of the resulting equivalent circuit. . .Historically, exterior dwelling GFCIs were mandated very early in the roll out, over the decades, of GFCI requirements.
They were mandated because practical cost effective technology became available to reduce the incidence of shock
it has worked
Excellent thread...
I am new to this forum... was browsing around and read this thread...
Now I understand why this forum was recommended.
THX to Mike and the moderators for the forum...
I can see this will be an asset to my small business in the future.
For now:
Merry Christmas,
Happy New Year,
Happy Holidays,
And an equal positive holiday wish to any other faith or belief I did not cover.
GA