The ampacity of 12 gage THHN is 30 amps, per 310.16, but
240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied.
(3) 14 AWG Copper. 15 amperes
(5) 12 AWG Copper. 20 amperes
(7) 10 AWG Copper. 30 amperes
Most electricans then state the ampacity of 12 AWG THHN is 20 amperes, when its actually 30.
This provision has been in the NEC for a long time, its only for 14,12 and 10 AWG, 18 and 16 were added in the 2008 NEC.
Why does the NEC restrict the overcurrent protection on these small conductors?