Agreed and this is the reason I do not think the guy is what he claims to be.A registered engineer working on electrical systems is probably versed at bonding and grounding issues.
For clearing faults, multiple parallel paths and loops are no issue.
Multiple parallel paths and loops may, however, cause problems with audio and radio installations. In radio, we try to use a 'single point ground' system. That's not self explanatory. But in a nutshell, we try to do away with as many parallel grounding paths and loops as we can. I heard the same is done on audio systems, but that's not my thing.
Depending on the frequencies of interest, yes, both radio and audio can benefit from a properly bonded/grounded single-point ground system.
I have an extensive system that I have to explain to PE's, EE's, and sparkies pretty regularly. Some see the IG receptacles and immediately call witchcraft...having no idea how to implement any of the basic methods in the Green or Emerald books at all.
All of my "engineering" experience came from working on the same equipment for about 28 years now. I am an electronics technician by paygrade, but engineer by job title.
Earthing is not in the question, it's about EGC's.We're not talking about supplementary (ie, not code required) ground rods are we? I was watching a MH video where he was showing that driving an extra rod, say at a generator, or for a PV array, could fry the electronics in event of a lightning strike. Lightning hits earth, travels up the ground rod at the generator/array, thru the circuitry, then back to the ground at the service.
We're not talking about supplementary (ie, not code required) ground rods are we? I was watching a MH video where he was showing that driving an extra rod, say at a generator, or for a PV array, could fry the electronics in event of a lightning strike. Lightning hits earth, travels up the ground rod at the generator/array, thru the circuitry, then back to the ground at the service.
So what exactly are we supposed to do. ith 690.47(D)anger? Put in the counterproductive superfluous electrode anyway, and then disconnect it after you get your approval?
Earthing is not in the question, it's about EGC's.
Roger
They are connected as a system Roger
I though that term referred to a single point of connection between the GEC, EGCs and the grounded conductor(s) and not to parallel paths in the equipment grounding system. Such paths are almost impossible to avoid unless you take special care in the design and installation of the system, especially where you are using wiring methods that are metallic and connecting to equipment with metallic cases.For clearing faults, multiple parallel paths and loops are no issue.
Multiple parallel paths and loops may, however, cause problems with audio and radio installations. In radio, we try to use a 'single point ground' system. That's not self explanatory. But in a nutshell, we try to do away with as many parallel grounding paths and loops as we can. I heard the same is done on audio systems, but that's not my thing.
I though that term referred to a single point of connection between the GEC, EGCs and the grounded conductor(s) and not to parallel paths in the equipment grounding system. Such paths are almost impossible to avoid unless you take special care in the design and installation of the system, especially where you are using wiring methods that are metallic and connecting to equipment with metallic cases.
From a noise perspective it is preferable to have "single-point grounding", with the system connected to the building ground wire at only one point. National electrical codes, however, often require all AC powered components to have third-wire grounds; from a safety standpoint it is preferable to have each AC component grounded. However the multiple ground connections cause ground loops when the components are interconnected by signal cables, as shown below.
250.6>
(B) Alterations to Stop Objectionable Current. If the
use of multiple grounding connections results in objection-
able current, one or more of the following alterations shall
be permitted to be made, provided that the requirements of
2S0.4(A)(S) or (B)( 4) are met:
(1) Discontinue one or more but not all of such grounding
connections.
(2) Change the locations of the grounding connections.
(3) Interrupt the continuity of the conductor or conductive
path causing the objectionable current.
(4) Take other suitable remedial and approved action.
I don't understand. I work in a plant that has all of those things operating without issues and there are hundreds if not thousands of parallel paths for the EGC.A 'ground loop' can be rather hard to mitigate, considering the construction methods of M.E.N. and S.D.S. 's prevalent to most American industry. Best examples are Cat 5e trunk lines, remote VFD & PLC's entering such structures all doomed from the start to sensitivity problems inherent in said design.
~RJ~