I don't understand where you can be coming up with this idea that a phase shift can exist without a time shift. That is exactly what a phase shift is! You shift the starting reference of one signal from another, and since our expressions for voltage are time-based, this is a time shift. (yes, in my previous posting I left the door open for your apparent phase shift that was actually an inversion.)
I am also quite perplexed about what you could possibly mean by a physical displacement as your phase shift. Sorry for the snarky comment, but does that mean you're going to move the wires some distance and call it a phase shift?
As it relates to the customary time-varying electrical expressions we use, please provide an example where a phase-shift is not a time shift. If the 180 degree shift is the only example you can come up with, that's because it is not a real phase-shift, as I have been saying. Do you have any situation that applies to this discussion where a phase shift is not a time shift?
First, there is a time shift from the primary to secondary that is an artifact of induction physics where the flux is not in phase with the voltage. We usually compensate for that by swapping the polarity or winding direction to have the primary and secondary in phase. So from the get-go, we are using a winding reversal to negate a real 180? phase shift.
So just on that, you could throw out the notion that a winding reversal does not give you a phase shift. However, we tend to ignore that phase shift so let's continue with some transformer phase shift references you can read that are talking about the phase shift caused by the physical voltage directions:
http://www.ece.msstate.edu/~donohoe/ece3414three_phase_transformers.pdf
The wye-delta and delta-wye configurations of three-phase transformers result in 30? phase shifts between the primary and secondary line-to-line voltages.
http://basler.com/downloads/3phXfmrs.pdf
Most engineers have some familiarity with two commonly known delta connections that give either a +30? or - 30? phase shift of positive sequence voltages and currents...The paper will review the variety of possible winding configuration and give examples of the nomenclature that is used with them and how these various phase shifts are created.
http://nptel.iitm.ac.in/courses/Web...l Technology/pdf/L-26(TB)(ET) ((EE)NPTEL).pdf
In the example shown, the phase shift of secondary winding is +30? with respect to the corresponding primary winding...
Considering the same example, if the primary delta connection had been made by connecting A2B1, B2C1 and C2A1, this would have resulted in a phase displacement of 30? clockwise(lagging) on the secondary side, i.e. the 1 o?clock position. This type of connection is termed asDy1 (Or Dyn1)
Westinghouse Distribution Transformer Guide:
2. Angular Displacement (Phase Shift)
For standard three-phase connections the phase-to-neutral voltage on the primary side either leads that on the secondary by 30? or is in phase with the phase-to-neutral voltage on the secondary side.
...
The delta wye and wye delta connections produce the 30? phase shift.
These are just a few examples from an untold number available.
In my open-wye to 4-wire wye, some of the voltages are:
Some linear voltages:
X1->X2 + X3->X4 = V@0? + V@0? = 2V@0?
X4->X3 + X2->X1 = V@180? + V@180? = 2V@180?
Some three-phase voltages:
X3->X4 = V@0?
X7->X8 = V@240?
X2->X1 + X6->X5 = V@180? + V@60? = V@120?
you will note that we have both the X1->X2 = V@0? and X2->X1 = V@180? voltages have physical phase displacments that produce voltages with physical phase displacements.
I can provide more examples but you should get the concept by now.
Another thing concerning time vs. phase:
A phase shift and a time shift go hand in hand but it really does depend on your reference frame. For example, in a three-phase generator all of the voltages start at the same time so they all have the same t
0. But from a different reference frame, we could consider the time that they peak. In that frame, the time of the positive peak (t
peak) will be different for the voltages. With the three-phase generator, we produce a shift by a physical shift, just like I did for the voltages on the left side of my generator example.
Using the winding voltages in different ways does not produce a real time shift for t
0 in one reference frame. But if we look at the positive peak times (t
peak) for those voltages, they do occur at different times.
The other way to get a shift is to actually delay the waveform. You could do this using delay boxes. I have a delay cascade circuit that I use on my workbench to get a 3-phase set of voltages from a single-phase source. The time shift due to flux lag from the primary to secondary side of the transformer is another example of a time delay.
This actual time delay appears to be the shift you are thinking about, but is not the phase shift we normally talk about when discussing transformer phase shifts. Outside of the shift from the flux delay (which we routinely ignore), the transformers do not have that kind of time shift.