... From answers.com and Britannica Concise Encyclopedia
That clearly states that to be in phase a peak has to correspond with a peak and a trough with a trough. Note: crest is the positive peak, and trough is the negative peak.
Note: the use of positive zero crossing as a usual time reference for one wave.
The BCE definition clearly shows the post being stuck on surface wave mechanics.
The Sci-Tech is a much better quote.
So I place the reference lead of my oscilloscope on A (v1) and measure both N and B (v2). I get two synchronous waves with identical phase angle and proportional magnitude. According to the BCE definition and Sci-Tech definition they are both "In phase" and have the same "Phase relationship".
So I place one oscilloscope across A (v1) and N. Then I place another oscilloscope across N and B (v2). I get two IDENTICAL waveforms. By BCE and Sci-Tech they are "In phase" and have the same "Phase relationship".
I am now Sooo happy you've cleared this up Gar. :angel:
Maybe I should move my reference leads to B (v2)? Will that help de-synchronize them? Or are you telling me that by moving your leads around you are somehow controlling the phase angles?
BCE is running two different waves down two different water boxes for their definition. For our purposes it should be ONE water box with a mark halfway down the length called Neutral. It then becomes obvious that it's just one wave traveling as it does in this circuit. And a single wave cannot be out of phase with itself.
Sci-Tech also says that you have to follow the time propagation of the wave "from an arbitrary time origin" and move "in the positive direction". From an electrical standpoint that means:
1) Choose either A (v1) or B (v2) as the "origin" and the other end of the secondary coil as the positive direction.
2) Your reference lead must always be to the "origin" side of the test lead.