caribconsult
- Añasco, Puerto Rico
- Retired computer consultant
We do have some brainiacs on this forum, that's true, and thank Mike for creating this.
yeah, I've seen em but to be honest, most techs are doing good to find the right setting in their meter. PCB level repair ain't gunna happen. BUT, it severely pizzed me off that they stuff the guts and highest failure mode device in the motor! If you work on these, you will understand that just getting the damn inverter off that motor would let it live, plus making it reasonable to replace or fix.Fastlane:
The older (1st generation ?) ECM blower motors had a "field replaceable" electronics pack, which an guy with an electronics background COULD field repair ( replace a blown thermistor and maybe a couple capacitors ). I did this a few times, as the upper board was only the power supply. The newer motors are potted, and this cant be done......... If you are talking about the older ECM's feel free to message me and I will give you the parts list...
Howard
On the "newer" ones, like the AC6000CW or SD80MAC; before that the motors were controlled by a setup which would connect the motor armatures and fields in various series/parallel combinations based on current draw (not directly by the throttle, that only controlled the prime mover speed).Basically the same concept as used on diesel-electric locomotives.
That word has been used well before using them in HVAC gear. Hell, go look at the Honda EU series generators from 25 years ago. Says "inverter" right on them.Mostly marketing. When these things were introduced they needed a term to distinguish them from legacy units. "VFD driven" was too much to explain to consumers. So Mitsubishi and others settled on the word "inverter" to described their new tech.
Invert in the electric world literally means "transform DC to AC", so ALL VFDs are "inverters". Hell, if you work around them, we use the terms interchangably. Drive - inverter - VFDYeah but those undeniably have inverters and are not variable fequency.
I don't really buy that 'inverter' is better marketing than 'VFD driven' from an *explanatory* viewpoint, but maybe it just focus-grouped better. Most consumers have no idea what either means so it comes down to vibes.
VFDs are a subset of inverters.
PSC likely less efficient than frequency driven. particularly when not running at speed corresponding to incoming frequency. But they are typically small motors to begin with and the question from owner's perspective is how fast to I recover my return on investment as the losses may be rather low. They likely less expensive to replace/repair as well.yeah, I've seen em but to be honest, most techs are doing good to find the right setting in their meter. PCB level repair ain't gunna happen. BUT, it severely pizzed me off that they stuff the guts and highest failure mode device in the motor! If you work on these, you will understand that just getting the damn inverter off that motor would let it live, plus making it reasonable to replace or fix.
As for standard split systems with an inverter driven compressor, they've yet to find a way to pack that in one screwjob package, but i'm sure it's coming. Hell, 20 years ago I was trying to just buy a simple, low tonnage 3P split so I could add a VFD.....Nope. Those just don't exist. I will tell you something, since most of the Copelands are 50/60hz rated anyway, that means I can walk one down there to 50 without any issue, and probably 45hz, meaning I could basically build a 2 stage system on the cheap.
And if you want to get 'real' cheap, you could just as easy step a PSC blower down with a relay. Oh the conspiracies.
Hi Garbo. I had similar experience but, in my case, it was based on industrial experience and mostly greater voltages up to 11k,Side note: the large hospital/research center that I retired from had over 500 VFD'S. Most drive manufacturers state the DC buss capacitors are rated for 75,000 hours we had probably close to a hundred VFD'S with over 125,000 hours. So they ran 24/7 for 15 years or more savings an incredible amount of money on power usage so am a huge fan of inverters ,drives, VFD'S even soft starters. I only wish that I would have wrote down hours , KW hours and motor ampere to figure out how much they saved as compared to a motor connected to a starter that is usually running at least with a 85% load. Heat & dirt along with loose connections are the biggest killers of drives & inverters. Only wish that drive manufacturers would use larger size wires especially on drives with three jammed in contractors behind a plate. While performing IR scans contactor area would be at least 15 to 20 degrees warmer then air conditioned space. They waited at least five years to purchase small air compressors that we kept on our PM carts. Even in clean air conditioned rooms was amazed the dust storm kicked out of VFD'S first time we blow them.out. Every VFD was blown out 1 to 4 times a year and in larger ones removed & cleaned filters on air intake fans. When contractors were performing demo.or producing dust we made them tape on 11/2" thick filter material on sir intake and replace it at least once a week. Was amazed when they retrofitted six twenty year old large boiler with VFD'S. They took an entire day on first change over where they monitored stack temperature and air samples while running boiler from 75# 's to normal 125#'s of steam pressure.
There isn't a significant eff boost in VFD motor loads. The eff comes from the variable capacity, and as mentioned, pushing a compressor beyond 60hz, which allows a smaller compressor to do the job. But anytime you make a volumetric refrigerant change, the airflow should be adjusted, thus ECM blowers were part of the equation. There are 2 stage systems in which the compressor has a partial bypass valve.PSC likely less efficient than frequency driven. particularly when not running at speed corresponding to incoming frequency. But they are typically small motors to begin with and the question from owner's perspective is how fast to I recover my return on investment as the losses may be rather low. They likely less expensive to replace/repair as well.
All VFDs can be called inverters. Not all inverters are VFDs. Like I said. So, no, not interchangeable. We solar guys installed thousands of inverters and would correctly never call them VFDs.Invert in the electric world literally means "transform DC to AC", so ALL VFDs are "inverters". Hell, if you work around them, we use the terms interchangably. Drive - inverter - VFD
Thus calling the drives in HVAC "inverters" is not wrong.....All VFDs can be called inverters. Not all inverters are VFDs. Like I said. So, no, not interchangeable. We solar guys installed thousands of inverters and would correctly never call them VFDs.
Lol ok, never said it was.Thus calling the drives in HVAC "inverters" is not wrong.....
This conversation is because you implied that 'inverter' on a Honda generator is the same as 'inverter' on a Mitsubishi heat pump, but it isn't exactly. Hmmm, maybe the term gained popularity because people liked those Honda generators. Has nothing to do with the reasons to use VFDs in HVAC units though.
I think what I was getting at is the PSC motor likely less efficient particularly if you are trying to vary it's speed (which PSC's are quite capable of) because "synchronus speed" doesn't change as the number of poles and frequency doesn't change. The motor is still trying to accelerate to synchronous speed but is being starved of enough input voltage by the method used to vary the speed that there is more slip. This will result in more current draw but at same time less voltage will also reduce current draw. Bottom line is a VFD driven motor still has less slip at those lower speeds but still has full torque in relation to what speed it is running.There isn't a significant eff boost in VFD motor loads. The eff comes from the variable capacity, and as mentioned, pushing a compressor beyond 60hz, which allows a smaller compressor to do the job. But anytime you make a volumetric refrigerant change, the airflow should be adjusted, thus ECM blowers were part of the equation. There are 2 stage systems in which the compressor has a partial bypass valve.
As mentioned, there are multiple advantages to VFD controlled systems, but that does come with additional failure points, and techs that probably won't be able to troubleshoot beyond reading the blinkies and calling the OEM.