According to the drawing, yes, that's why. The two disconnects on the pedestal need to be in one enclosure.Is it because there are 2 separate service disconnects where the feeders originate?
Please explain why.If you made one of those service disconnects a transfer switch for a generator it would be legal.
And why is that?According to the drawing, yes, that's why. The two disconnects on the pedestal need to be in one enclosure.
225.30(A)(4)Please explain why.
View attachment 2559053
Is it because there are 2 separate service disconnects where the feeders originate?
Confused.
JAP>
Yes, confusing. If the 2 feeders came from one disconnect enclosure you can actually have 6 separate enclosures at the building with main disconnects
I agree confusing.
There is no such thing as 2 feeders from a single disconnect unless you bring the Tap rule into play.
If you had (2) feeders where the tap rule didn't come into play the feeder conductors would have to be full size to the structure so what's the point?
JAP>
You said from (1) Disconnect.If you have a main breaker panel and run 2 feeders from the panel are you saying you can't do that? lol
I don't think they mean a one circuit panel.
Plus the now in the 2020 NEC we cant have the two 200A mains in one 400A main lug enclosure anymore
Okay a technicality-- a main panel can have a disconnect and other spacesYou said from (1) Disconnect.
A Disconnect is not a Breaker Panel.
JAP>
2 feeders came from one disconnect enclosure
Okay a technicality-- a main panel can have a disconnect and other spaces
Here is what I said and obviously I could have been clearer
Could you just eliminate the disconnects at the meter?
Yes and then you would have service conductors not feeders and you wouldn't be allowed to run 2 sets of service conductors to a building. Unless that has changed in the 2020
I am thinking call it one 'set', as they are joined at the 320A meter end.Yes and then you would have service conductors not feeders and you wouldn't be allowed to run 2 sets of service conductors to a building. Unless that has changed in the 2020
Exception No. 2: Where two to six service disconnecting means
in separate enclosures are grouped at one location and supply
separate loads from one service drop, set of overhead service
conductors, set of underground service conductors, or service
lateral, one set of service-entrance conductors shall be permitted
to supply each or several such service equipment enclosures.
However, in most cases, two service disconnects, in that size range, in one enclosure will violate 230.71(B) in the 2020 code.According to the drawing, yes, that's why. The two disconnects on the pedestal need to be in one enclosure.