hardworkingstiff said:Yup e57, that's what I was thinking about. I don't remember ever seeing a closed delta service. Most of the deltas I've seen have been in commercial buildings with a small 3-phase load, I guess that's why.
The code section for B phase being the high-leg is 408.3(E). I remember in the 70's, it was C phase.
Exception: Equipment within the same single section or multisection switchboard or panelboard as the meter on 3-phase, 4-wire, delta-connected systems shall be permitted to have the same phase configuration as the metering equipment.
Are you sure? Around here the high leg is landed on the C phase postition because of the metering requirement, however you will find that it really is B phase if you put a rotation meter on it.Around here the original POCO installs are High-C phased, and often if there is an existing transformer they will continue to use C rather than break out the rotation meter
don_resqcapt19 said:e57,
Are you sure? Around here the high leg is landed on the C phase postition because of the metering requirement, however you will find that it really is B phase if you put a rotation meter on it.
Don
At the transformer they are connected A, B, C, at the metering equipment they are landed A, C, B and at the service disconect they are landed A, B, C. The only place the rotation is different is from the line side of the metering equipment to the line side of the service disconnect.if you move B to C, and still call it B, you need to move/swap the other two and rename them too.
Actually it is required by the code. See 408.3(E), 430.97(B) and 409.102(B)Which brings up a great point, never thought of "rotation" being required, if it isn't it should be. The NEC is not specific on it.
Don408.3(E) Phase Arrangement The phase arrangement on 3-phase buses shall be A, B, C from front to back, top to bottom, or left to right, as viewed from the front of the switchboard or panelboard. The B phase shall be that phase having the higher voltage to ground on 3-phase, 4-wire, delta-connected systems. Other busbar arrangements shall be permitted for additions to existing installations and shall be marked.
don_resqcapt19 said:e57,
At the transformer they are connected A, B, C, (Clock-wise) at the metering equipment they are landed A, C, B (Counter Clock-wise) and at the service disconect they are landed A, B, C. (Clock-wise) The only place the rotation is different is from the line side of the metering equipment to the line side of the service disconnect.
Actually it is required by the code. See 408.3(E), 430.97(B) and 409.102(B) (2005?)
Don
(2002 commentary) The high leg is common on a 240/120-volt, 3-phase, 4-wire delta system. It is typically designated as ?B phase.? Section 110.15 requires the high-leg marking to be the color orange or other similar effective means of identification. Electricians should always test each phase to ground with suitable equipment in order to know exactly where this high leg is located in the system.
The exception to 408.3(E) permits the phase leg having the higher voltage to ground to be located at the right-hand position (C phase), making it unnecessary to transpose the panelboard or switchboard busbar arrangement ahead of and beyond a metering compartment. The exception recognizes the fact that metering compartments have been standardized with the high leg at the right position (C phase) rather than in the center on B phase.
See also 110.15, 215.8, and 230.56 for further information on identifying conductors with the higher voltage to ground. Other busbar arrangements for making additions to existing installations are permitted by 408.3(E).
It is my opinion that the code requires that when you hook up the phase meter with the leads landed in order left to right, that the meter should indicate A B C rotation. Of course the exception would apply if the meter is part of the service equipment or if you are adding to an existing installation. The only high leg services that I have worked on have used self contained meters and in that case the code requires A B C rotation at the service equipment.Simularly if you had High-B, the code doesn't state specificaly that it needs to be clock-wise or counter clock-wise. Calling a phase A, B, or C is arbitrary until it lands in a panel, disco or secondary transformer in the building. If you are handed 4 unmarked conductors from the POCO, one being grounded, another a high-leg, and you make that your B phase - the code doesn't say what the other two should be.
If the A B C in the above is not phase rotation, what is it?(E) Phase Arrangement The phase arrangement on 3-phase buses shall be A, B, C from front to back, top to bottom, or left to right, as viewed from the front of the switchboard or panelboard. The B phase shall be that phase having the higher voltage to ground on 3-phase, 4-wire, delta-connected systems. Other busbar arrangements shall be permitted for additions to existing installations and shall be marked.
don_resqcapt19 said:e57,
If the A B C in the above is not phase rotation, what is it?
Don
As there is no reasonable way to identify A phase, all ABC requires is that the left phase leads the center by 120 degrees and the center leads the right by 120 degrees. ABC=BCA=CAB and are all code compliant. CBA=ACB=BAC and would all be violations.I infer that Va leads Vb by 120 degrees. Right? Then C B A would mean that Vc leads Vb by 120 degrees. Right? I hope so.
I think that is where it implies rotation, but fails to state "rotation". It wants >ABC, but fails to state it can not be <ABC. And goes further with the exception to say within the same premises essentially you could have the high leg on B or C if the meter and associated sections are set up as C. Or what to do with the placement or marking of the other two once they leave the meter cabinet or panel. It only mentions the placement of one leg if higher to ground. And says nothing with, or without a high leg about "rotation" specifically.don_resqcapt19 said:e57,
If the A B C in the above is not phase rotation, what is it?
Don
don_resqcapt19 said:rattus,
As there is no reasonable way to identify A phase, all ABC requires is that the left phase leads the center by 120 degrees and the center leads the right by 120 degrees. ABC=BCA=CAB and are all code compliant. CBA=ACB=BAC and would all be violations.
Don
LarryFine said:Me again. I couldn't sleep.
What I mean is, let's take an open Delta. We know the primary is two phases, but which two? Does it matter? We know the timing is 120, 240, 120, 240..., but do we know whether the main or high-leg secondary leads or follows? Again, does it matter?
When we bring the service to the premises, of course we need to know which is the high leg, but do we know which pair of lines straddle the missing secondary? Do we need to know? Do this and the rotation direction have any interaction? I think not, myself.
I've seen that the POCO strives to keep one phase in the center on the poles, but I've also seen them cross. When they branch off two for an open-Delta line, which two? How do they keep track of which is which throughout the line? Do my questions make sense?
"How do it know?" :-?
e57 said:And you NEED 3 primaries for an open or closed delta.