Bob, I think I have been saying the same thing? Or trying to. But if you have a high-leg you can choose to call it B or C, and A will be different depending on that choice. Choose poorly, and you have counter clock-wise. Which is why I often go to a building to put in say an air conditioner, and have to double and triple check rotation before I leave so we don't end up owning that AC unit. If rotation were standard I could walk in ABC-123, and leave.iwire said:Mark I think, and Larry feel more then free to correct me here, the question becomes which phase is really 'A'?
In my experience the power company does not identify any phase as A B or C.
I can certainly get clockwise rotation without knowing which phase is actually A B or C.
Likewise the NEC does not dictate color codes to us spare a few, two of which are in a high-leg system. (neutral and a high-leg) And on those it matter which is which. But changing the other two changes rotation and it too can matter which is which. (Moving the high-leg C-B after a meter cabinet changes rotation.) But the code doesn't actually come out and say it needs to be and maintain one direction over the other.
Heres my local code pet peev -
120/240 volt 3-phase delta circuits - “A” phase black, “B” (high leg) phase purple, “C” phase red
hardworkingstiff, I am not sure I have ever seen a set up like that, and don't think it could be called 3 phase without having all 3 phases present.