I have a unique situation. Kitchen counter is 27 " deep . The top of the counter will be 3/4" below the window after it is trimmed. The homeowner wants a deeper sill so the sill will come out about 3" onto the top of the counter.
So-- no place for a receptacle, right--- Architect came up with an idea that I feel uneasy about, but I think is legal. Put a receptacle face up in the window sill--art. 406.4 says NO to countertops and similar work spaces. I may have a loophole here.
Here is the receptacle & website link--