Conductors in conduit are accessible per this defintion.Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.
don_resqcapt19 said:Chris,
Are you saying that we can't remove wire from a conduit without damaging the building?
Conductors in conduit are accessible per this defintion.
Don
raider1 said:If I install cables within a conduit aren't they closed in by the building structure or finish?
Chris
iwire said:Chris I have to agree with Don here.
The wires in conduits are capable of being removed without damaging the building. That means they are accessible.
OR
If it was NM we had to remove and it was not permanently closed in by the structure or finish of the building then it would be accessible.
raider1 said:I'm not following the last part of your comment.
Chris said:The definition has two parts part one is capable of being removed or exposed without damaging the building structure or finish and the second is not permanently closed in by the structure or finish of the building.
So abandoned cables installed within conduit increases the spread of fire within a building?
iwire said:It says what it says, everything else is just noise.
raider1 said:I have a bad habit of trying to understand the reason for a particular code section.
Fire Alarm said:You can always leave the cables in place and tag them for future use.
Sometimes sense just can not be made of it, in the same occupancy they are worried about the smoke load produced by cables in the ceiling, conduits etc the people are long since dead from the smoke produced by all the stuff out in the open that produces smoke.