Tape Brn/Org/Yel #12's together as a set and pulling 3 of these sets
into a 3/4" conduit
Yep, you could even do it in 1/2.
Since a ground would also be required, that would be 10 total which does not fit in 1/2" EMT or PVC (longer than 24"). OP didn't specify conduit type.
Wire egc not required for emt, of course....
Can you tape the Brown/Orange/Yellow #12 THHN together and pull 3 sets of these in a 3/4" Conduit?
Yes. With some adjustment.
.
Table 310.15(B)(3)(a)
7-9 conductor, 70%
#12 use 25 amp X 70% = 17.5 amps
Do what you want but if I'm using a 90C conductor such as THHN I'm going to use
30 amps X 70% = 21 amps
What are you terminating that wire on both ends?:huh:
90 degree can be used for derating. 9 CC is the magic number for #14 and #12. So in practice, most of the time, I can pull 3 full boats of 12 or 14 with no derating.
90 degree can be used for derating. 9 CC is the magic number for #14 and #12. So in practice, most of the time, I can pull 3 full boats of 12 or 14 with no derating.
I stand corrected.
Terminal rating is not involved?
When I do that I identify each "set" with a different color tape around each set.Tape Brn/Org/Yel #12's together as a set and pulling 3 of these sets
into a 3/4" conduit
Since a ground would also be required, that would be 10 total which does not fit in 1/2" EMT or PVC (longer than 24"). OP didn't specify conduit type.
dont pools and such need insulated EGC (if the work was for a pool)?Please cite the code section where a ground wire is required in EMT?