Wire size and ocp for VFD
Read The "Factory" Manual.
(Generally, the "F" stands for something other than Factory though...)
This piece of equipment, including the drive was installed and an electrical contractor made the electrical connections years ago, awhile back we experienced some power issues to this building; lost phase. When the power came back up AHU-1 did not start, shop HVAC tech found blown 90a fuse, fuse was replaced, power was turned on and POW, drive smoked. The tech was concerned about the wire size (3-#6's and a #12G) on 50 amp breaker. I have been tasked with correcting the obvious problems with wire size and breaker size. The electrical drawings show 1 20hp motor when there are 2, it also shows 3-#8's and #10G. I have been working with the in house electrical engineer to try and figure out how this happened and who is responsible. I have been reading the "Factory" manual and see that there may be other issues with this install, the wire from the motors to the drive are separate #8 thhn with #10G tie-wrapped together and secured to the inside of the motor enclosure. The engineer stands by his recommendation of 3-#4's and #6G on 110a breaker. The "Factory" manual states: AC Mains Connection- Size wiring based upon the input current of the frequency converter. I will admit I do not have much experience with drives, what I know now is from reading information from the TRANE website on the TR200.
My guess was drive was already smoked and that had a lot to do with why fuse was blown. By replacing fuse and energizing he just got to see why the fuse was blown the first time.
The equipment has ran for the past 3 years as wired, we do have our issues with power quality, loss of phase, dips and spikes.
RTFM or "reading the factory manual" TR200
Still working on this, still confused, according to the "Trane Drive operating Instructions", 2.4.4 AC Mains connections: Size wiring based upon the input current of the frequency converter. For maximum wire sizes see 10.1 Power-dependent specifications. Going to page 69 table 10.6 Mains Supply 3X380-480 V AC, in the P37K column, Max. Input current, Continuous(3X440-480V) [A] is 59 Intermittent(3X440-480V) [A] is 64.9
KISS it! (keep it stupidly simple) The code requires you to size the supply conductors to the VFD based on the VFD rating x 1.25 (430.122). If you have a 59A VFD, that's just what you need to install for. That intermittent rating is just an overload capacity of the drive which is 10% of its continuous rating.
Another acronym, not the way I heard it said but I like your definition better. VFD input current= 170.2A X 1.25 =212.75 seems awful high for something driving 2-20hp motors, been doing a lot of reading on this subject seems I'm not the only one confused. As I said previously, this was install and wired years ago and until recently it worked fine as wired; although the equipment ground was the wrong size for a 50a breaker.
Here is something I found that seems to contradict what some people have said:Sizing conductors for VFDs
We have a motor control center (MCC) where we removed the combo starters and landed the wire directly to the circuit breakers and then to a variable frequency drive (VFD). These breakers are all inverse-time breakers, and in referencing the Code, I am using Sections 240.6, 430.52(C)(1) and Table 430.52 to confirm that no breaker or wire size is over the 250-percent rule for inverse-time breakers. Here is an example: from a 70-ampere (A) breaker in the MCC, 8 AWG wire was run to a disconnecting means where we have now installed a VFD. The motor at full load does not draw more than 37.8A at 480 volts (V). We are being told that we are in violation of Section 430.122 and that all wiring from the MCC to the VFD needs to be replaced. What is the correct answer?
The full-load current of the motor must be taken from Table 430.250. You didn’t give the motor horsepower, but I am assuming it is 30 horsepower from the 37.8 full-load amperes you present. The full-load current from Table 430.250 for a 30 horsepower, 460V motor is 40A. Using Table 430.52, the maximum rating permitted for the branch-circuit short circuit and ground-fault protective device using an inverse-time breaker is 250 percent, which allows a 100A rated overcurrent device (40 2.50 = 100). The size of the motor-circuit conductors is determined by 430.122, which requires an ampacity rating of 125 percent of the motor full-load current taken from Table 430.250. The ampacity of the branch-circuit conductors is required to be 40 1.25 = 50A. This permits the use of 8 AWG conductors.
... Here is an example: from a 70-ampere (A) breaker in the MCC, 8 AWG wire was run to a disconnecting means where we have now installed a VFD. The motor at full load does not draw more than 37.8A at 480 volts (V). We are being told that we are in violation of Section 430.122 and that all wiring from the MCC to the VFD needs to be replaced. What is the correct answer?
430.122 essential trumps the other rules because things are different with a VFD. You can use a VFD at its rated output current, but because everything is programmable, that may or may not relate directly to the actual motor size. For example I can install a 50HP rated VFD and use it on a 25HP motor. If I sized the conductors for the 25HP motor, the input current for the VFD might become higher than that some day in the future if someone changes the motor to 30, 40, or 50 HP because they see that the VFD is rated for that. The input conductors would be too small then. So the NEC addressed this by requiring, in 430.122, that those conductors FEEDING the VFD must be sized based on the VFD maximum input amp rating. But remember, this is only pertaining to the MINIMUM size of the CONDUCTORS, not the circuit protection.
Down stream of the VFD, the drive is protecting the motor, and the drive is controlling the amps, including starting current. Think of the VFD as a completely new power source for the motor, with its own protection scheme. The feeder breaker size then need only be based on what the DRIVE needs on the input side, not the motor. I've heard (but not yet seen) that the next code revision is going to address the OCPD sizing for the DRIVE, but at this point it is not there yet. That's why you just stick to what the drive is listed with, which should be in their manual (assuming it is UL listed, because UL requires it).
VFD input current= 170.2A X 1.25 =212.75 so why are the fuses at 1F40,1F41,1F42 JJS-100
40HP worth of 460V motors does NOT need a VFD rated for 172A, something is wrong there. The VFD would only need to be rated at around 52-60A at most. It says on the nameplate that the motors themselves are rated 27A each, so that's 54A total if there are two.
My take is that the 172A is the current for the ENTIRE unit, INCLUDING the VFD. If so, then that ALREADY has the VFD / motor load buried in the combination rating and falling under 430.110(C).