elevate said:Is there a wire size limit on a temporary installation according to NEC. We Have some motors that need to keep running while utility works on transformer.
Yeah, you really gotta be careful and keep your eyes peeled. So many guys are trying to sneak in the use of that 2001 kcmil for their temp installs.Pierre C Belarge said:Yes, from 14AWG - 2000 kcmil :wink:
mdshunk said:Yeah, you really gotta be careful and keep your eyes peeled. So many guys are trying to sneak in the use of that 2001 kcmil for their temp installs.
mdshunk said:Yeah, you really gotta be careful and keep your eyes peeled. So many guys are trying to sneak in the use of that 2001 kcmil for their temp installs.
elevate said:Is there a wire size limit on a temporary installation according to NEC. We Have some motors that need to keep running while utility works on transformer.
Some guys get to have all the fun!iwire said:It happens the company I work for does this all the time for a power company.
LarryFine said:Some guys get to have all the fun!
Sounds a lot like some alien abduction stories.iwire said:One minute I am home sleeping, the next thing I know I am driving two hours to connect 2MW genset to a rock crusher at 1AM in a dark gravel pit.
brother said:I always thought these temporary installs had to us more tuffer type of cable when ran like this. Is this just the same type of 4/0 cable you would use if you were putting in perminant installs in conduit??
mdshunk said:Sounds a lot like some alien abduction stories.
What is the address again????iwire said:It is portable power cable, it's like welding cable with a 600V rating. :smile:
I would hate to have to pull it in conduit as the insulation is rubber and does not slide well. A 50' section weighs just under 60 Lbs.
brother said:I always thought these temporary installs had to us more tuffer type of cable when ran like this. Is this just the same type of 4/0 cable you would use if you were putting in perminant installs in conduit??
don_resqcapt19 said:Bob,
Per Table 400.5(B) I would not accept 360 as the ampacity of those cable where installed as shown in the photos. I am not sure what the ampacity would be as the table does not directly cover your installation.
It appears to me that the individual conductors are in contact with each other for more than 24" in many places in the picture. I don't see any column ampacities that apply directly to the installations in your photos.1The ampacities under subheading D shall be permitted for single-conductor Types SC, SCE, SCT, PPE, and W cable only where the individual conductors are not installed in raceways and are not in physical contact with each other except in lengths not to exceed 600 mm (24 in.) where passing through the wall of an enclosure.
don_resqcapt19 said:It appears to me that the individual conductors are in contact with each other for more than 24" in many places in the picture.