brother said:I always thought these temporary installs had to us more tuffer type of cable when ran like this. Is this just the same type of 4/0 cable you would use if you were putting in perminant installs in conduit??
mivey said:iwire,
How do you keep people out of the secondary cabinet? What is done about the back-fed primary side of the xfmr and the metering equipment?
don_resqcapt19 said:Because of note 1 that applies the column D ampacities. It appears to me that the individual conductors are in contact with each other for more than 24" in many places in the picture.
I don't know of any equipment that will let you use the 90?C rating, except for the purpose of derating.zbang said:I have some Carol type SC 1g that's marked ""NEC 400-5(b) for 90degC outdoor". Assuming that the 4/0 is similarly marked, this would put 4/0 at 405a. Some people will also argue that the conductors are effectively unbundled, and thus in "free air". But I won't :grin:. I will also dodge the question of derating.
Ah. The Artful Dodger.zbang said:I will also dodge the question of derating.
brian john said:We do this all the time, once did 21 cables 4/0 360' one way distance, wears me out.
Given the price of copper now, unless you hire an armed guard, you won't have any pick up to do:smile:iwire said:It does beat you up, especially the breakdown and roll up of all the cables.
don_resqcapt19 said:Given the price of copper now, unless you hire an armed guard, you won't have any pick up to do:smile:
don_resqcapt19 said:Given the price of copper now, unless you hire an armed guard, you won't have any pick up to do:smile: