Wire Size

Here is the complete schedule.


1. FLC is NOT listed only FLA. You state it's to be sized off FLC and NOT FLA.
2. For some reason HP is not indicated.


View attachment 2580390
FYI this is exactly what I posted for. I am not picking on you, but instead informing you that information out is only as good as information in, and this proves that. When you question sizing for this table, it is only about MCA and FLA. The designer already di all other work for you.
and this table doesn't show the same information for the EF as your original pot. They are different tables.
 