Hey guys just want to make sure i am doing this wire way fill correctly...
I have the following in it.
12- 4/0 THHN
4- #3
12 x .3237= 3.8844
4 x .0973= .3892
4.2736 / .20= 21.368 in. 2
which means i would need a 6" x 6" trough.
Now what i ahve is a MDP that is feeding a few panel in an electric room and the trough is running above all panel and i am going to nipple up to the trougn from each panel. Now the distance from where the conduit enters the trough to the opposing wall is determined from 312.6a which would be 4" right seem strange that they allow us to use the one terminal row when i have 4 wires leaving each conduit...
I have the following in it.
12- 4/0 THHN
4- #3
12 x .3237= 3.8844
4 x .0973= .3892
4.2736 / .20= 21.368 in. 2
which means i would need a 6" x 6" trough.
Now what i ahve is a MDP that is feeding a few panel in an electric room and the trough is running above all panel and i am going to nipple up to the trougn from each panel. Now the distance from where the conduit enters the trough to the opposing wall is determined from 312.6a which would be 4" right seem strange that they allow us to use the one terminal row when i have 4 wires leaving each conduit...