is there a single conductor direct buried wire? Can I buy just one conductor to be put in the ground? I need to add a # 6 for an existing three wire 200 amp service going to a residential sub panel
is there a single conductor direct buried wire? Can I buy just one conductor to be put in the ground? I need to add a # 6 for an existing three wire 200 amp service going to a residential sub panel
is there a single conductor direct buried wire? Can I buy just one conductor to be put in the ground? I need to add a # 6 for an existing three wire 200 amp service going to a residential sub panel
no you can't,all feeders would have to be in same jacket or conduit etc.in case a fault occurs between any feeders!!!is there a single conductor direct buried wire? Can I buy just one conductor to be put in the ground? I need to add a # 6 for an existing three wire 200 amp service going to a residential sub panel
no you can't,all feeders would have to be in same jacket or conduit etc.in case a fault occurs between any feeders!!!
Not if direct buried.
What do you mean by add? How are the other conductors ran?
no you can't,all feeders would have to be in same jacket or conduit etc.in case a fault occurs between any feeders!!!
Not if direct buried. What about a line to EGC fault?
If the other circuit conductors are in a cable assembly the EGC has to be as well.
I'll bet he is wiring a swimming pool off the sub panel
not going to be buried, the pvc is underground to the house then its attached to the floor, ser is attached and secure to the floor
I don't think you can put SER in conduit that is buried. You would need USE cable.
338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-entrance cable (SE)
shall not be used under the following conditions or in the
following locations:
(2) Underground with or without a raceway
I don't think you can put SER in conduit that is buried. You would need USE cable.
they are in ser cable 150' of it. from outside they go through 2" pvc, under the house about 40' in the pvc stops and the ser continues on up into the panel, and its three conductor so I am adding a # 6 ground