If the other circuit conductors are in a cable assembly the EGC has to be as well.
they are in ser cable 150' of it. from outside they go through 2" pvc, under the house about 40' in the pvc stops and the ser continues on up into the panel, and its three conductor so I am adding a # 6 ground
For new work iwire is correct.
But I remember there used to be an exception for old work such as this (maybe local) where the EGC was allowed to run on the outside of cable assembly and wire tied to the cable. There were and are a lot of older sub panels without EGCs.
I would call the local inspectors and see what they will allow for this. They are often more permissive on old work. Tell them some idiot in Georgia mentioned it and you want to see if it will fly locally.