in the past three conductors was permitted to feed sub panel, now all are required to have a four wire feed yes?
Up thru 2005, yes. That changed in 2008- it's allowed only if it was existing, must have the egc for new sp's.
in the past three conductors was permitted to feed sub panel, now all are required to have a four wire feed yes?
:thumbsup:
Is there any particular reason / real life consequence as to why SER / SEU is not allowed underground even in a raceway? The constituent XHHW-2 wires inside of it would be allowed underground in a raceway on their own.
Would it be permissible to strip away the SER jacket and continue the constituent XHHW-2 wires underground in a raceway?
Up thru 2005, yes. That changed in 2008- it's allowed only if it was existing, must have the egc for new sp's.
so there is not a bare conductor with two insulated conductors? wrapped in a gray sheath?
I think I let one of my designs slip through the cracks with SER spec'd in an installation that is mostly above ground, and part of it had a 10 ft "dive" below ground
Werent subpanels permitted to be fed from 3 conductor cable in the past?
but note that is for feeders between different structures. Separate N/G has been required for same-building sub panels for a long time.
NoIn general, can a bare aluminum EGC be used below grade? ....
250.120 Equipment Grounding Conductor Installation
(B) Aluminum and Copper-Clad Aluminum Conductors.
Equipment grounding conductors of bare or insulated alumi-
num or copper-clad aluminum shall be permitted. Bare con-
ductors shall not come in direct contact with masonry or the
earth or where subject to corrosive conditions. Aluminum or
copper-clad aluminum conductors shall not be terminated
within 450 mm (18 in.) of the earth.
Yesin the past three conductors was permitted to feed sub panel, now all are required to have a four wire feed yes?
YupUp thru 2005, yes. That changed in 2008....
CorrectYes, but that was only allowed if there wasn't any parallel ground paths like a water pipe, phone wire or cable tv.
...but note that is for feeders between different structures. Separate N/G has been required for same-building sub panels for a long time..
:thumbsup::thumbsup:There was a thread about this recently- looked this up then and found no evidence 3 wire to sub in same structure was ever permitted or at least it wasn't enforced in many areas.
338.12 [Uses Not Permitted] was added in 2008. The reason for not using SE underground prior to 2008 did not exist. :angel:I used SER in pipe below ground (about 10 feet) back in 2007. I think that is before the wording was changed, at least that is my excuse :angel:. It still haunts me every day.
338.12 [Uses Not Permitted] was added in 2008. The reason for not using SE underground prior to 2008 did not exist. :angel:
250.120 Equipment Grounding Conductor Installation
(B) Aluminum and Copper-Clad Aluminum Conductors.
Equipment grounding conductors of bare or insulated alumi-
num or copper-clad aluminum shall be permitted. Bare con-
ductors shall not come in direct contact with masonry or the
earth or where subject to corrosive conditions. Aluminum or
copper-clad aluminum conductors shall not be terminated
within 450 mm (18 in.) of the earth.
Sort of moot point to discuss, not being able to use underground now and all, eh?Oh grand, it is true and I didnt just subconsciously make that up!
I was pretty sure that was the case but was too lazy to double check. So back to the SER, It seems that as Carultch was proposing, if one really wanted to get one up on the man and/or cause trouble, he or she could re-identify one of the insulated conductors as the EGC, and get away with using it in pipe below grade? (looking for the devil smiley, alas guess it doesn't exist....)
I think because it was design for free air, like uf can't go in pipe!Oh grand, it is true and I didnt just subconsciously make that up!
I was pretty sure that was the case but was too lazy to double check. So back to the SER, It seems that as Carultch was proposing, if one really wanted to get one up on the man and/or cause trouble, he or she could re-identify one of the insulated conductors as the EGC, and get away with using it in pipe below grade? (looking for the devil smiley, alas guess it doesnt exist....)
I think because it was design for free air, like uf can't go in pipe!
Sort of moot point to discuss, not being able to use underground now and all, eh?
Up thru 2005, yes. That changed in 2008- it's allowed only if it was existing, must have the egc for new sp's.
where is that in the code book? I need to show this to the home inspector and thank you
Oh grand, it is true and I didnt just subconsciously make that up!
I was pretty sure that was the case but was too lazy to double check. So back to the SER, It seems that as Carultch was proposing, if one really wanted to get one up on the man and/or cause trouble, he or she could re-identify one of the insulated conductors as the EGC, and get away with using it in pipe below grade? (looking for the devil smiley, alas guess it doesnt exist....)
Doesn't change the fact it is SE cable and not permitted underground, does it?If it has marked XHHW inners and I don't have a bare egc, than it seems plausible that then it's just XHHW conductors in conduit with some superfluous gray sheath.