codetalker
Member
- Location
- spokane
30A dual pole 240v, running #10 NM to a relay (in a metal box) for electric heating (15.8A), the relay RC840 is good for 22A. I'm using #10 wire because I can and for voltage drop. The relay unit has #12 (built in pigtail) for hookup. Obviously if there is a short somewhere this #12 wire becomes a concern. There is no recommended wire size for relay install. Working on the best approach for protection; use a 20A breaker on #10 wire? Inspection to follow.
Thanks