I've seen a number of houses where the electricians wired the entire house with 12AWG, rather than using #14 for the lighting circuits. This makes NO sense to me at all why anyone would do that. Wiring the receptacle outlets with 12AWG is great, as long as they are separated from lighting. Then wire the lighting circuits with #14 wire, separate from any receptacles or other loads (other than smoke alarms and a doorbell).
The main problems with wiring lighting circuits with #12 are:
1) Extra cost for #12 cable versus #14
2) Extra difficulty in working with #12 vs. #14, especially in multiple-gang switch boxes containing lots of wires
3) Box-fill issues. The same number of #12 conductors will NOT fit into a box of a given size filled with #14 conductors.
In reference to #3 above: For example, if wiring a lighting circuit, and using a 2-gang blue Carlon switch box, it can hold 16 #14 conductors. Let's say the circuit design calls for four 14/2 cables and one 14-3 cable in the box. This would add up to 16. Therefore, the same design could NOT be implemented using #12 wiring without using a larger size box.
The main problems with wiring lighting circuits with #12 are:
1) Extra cost for #12 cable versus #14
2) Extra difficulty in working with #12 vs. #14, especially in multiple-gang switch boxes containing lots of wires
3) Box-fill issues. The same number of #12 conductors will NOT fit into a box of a given size filled with #14 conductors.
In reference to #3 above: For example, if wiring a lighting circuit, and using a 2-gang blue Carlon switch box, it can hold 16 #14 conductors. Let's say the circuit design calls for four 14/2 cables and one 14-3 cable in the box. This would add up to 16. Therefore, the same design could NOT be implemented using #12 wiring without using a larger size box.