On that, I agree.Which doesn't make much sense because EMT can be run through bored holes in studs without the 1.25" setback.
While EMT "bushings" may appease some inspector(s), the pieces are technically not EMT unless installed as a complete run. As suggested, those 2.5 inch long pieces of EMT are just steel bushings... so they do not qualify under Exception No. 1, not are they the required 1/16" thick. You'd have to use bushings made of rigid steel conduit to meet the 1/16" thickness requirement.
It's not the length. It's whether or not it installed as a complete run. That's the way the Code reads. Don't shoot the messenger.How does the length of the conduit affect its listing? If I had a 4" piece of EMT coming from breaker panel, thru a stud, and into a 1900 box, it would be okay, but a 4" piece of EMT to protect NM thru a stud isnt kosher?
You are correct. I said what I said because IMC isn't as commonly available in a lot of locations, and if you want to bore a 1.510" diameter hole for a single NM cable, go for it.Also, EMT that is 1.25" or larger has a wall thickness of 1.65mm. IMC of any trade size is >1.6mm; no need for RMC.
If I have a UL listed panelboard and use it as a doorstop, is it a panelboard because it is UL listed as such or is it just a doorstop.Can you point us to a section that says the item with a UL tag that says EMT is not EMT?
Same goes for EMT.
Then you have 358.30 general statement which leads ultimately to 300.18(A).
Same goes for EMT.
You're right. It is still a panelboard... but it is being used only as a doorstop and not subject to NEC purview as such. In effect, not a panelboard.It is still a panelboard you happen to be using for something else.
But stick with EMT it is EMT regardless of its use. If it is a compleate raceway system is another matter.
See above.300.18 exception:
"Short sections of raceways used to contain conductors or cable assemblies for protection from physical damage shall not be required to be installed complete between outlet, junction, or splicing points"
Securely fastening a short section of pipe may be a challenge; I dont suppose a near press-fit of the pipe thru the horizontal hole would be acceptable. or do such bushings or nipples have to be supported at all?
Exactly... but in a pinch, it provides a Code-compliant option.This is all academia anyway; I do not know of anyone who would go thru the trouble of a metal bushing in wood when a 16 cent nail plate that takes 10 seconds to install would do.
I think I'm make a call to the inspector who signed off on the rough in and see if he requires them. He will be doing the finial inspection when ready.
There's more in the NEC to back up my assertion than there is yours....
There is nothing in the NEC to back that up.
A steel nipple would have to be grounded equally to the conductor ampacity on both ends. It's nonsense, whatever he thinks.
Sent from my XT1080 using Tapatalk
Something tells me legs are getting pulled.:happyyes: