All of which do not have working clearance issues brought up by the OP
None of these power transformers have viewing windows
Sent from my iPhone using Tapatalk
All of which do not have working clearance issues brought up by the OP
Isn't adding them an easier option if leaving the access gate/door isn't allowable?None of these power transformers have viewing windows
Agreed. I like viewing windows personally. If it's an issue they are easily added. Post 13-16.Thermal scans of connections while under load would have to be done while energized.
Isn't adding them an easier option if leaving the access gate/door isn't allowable?
Isn't adding them an easier option if leaving the access gate/door isn't allowable?
It is all but impossible to idiot proof an installation.Inevitably there is some idiot out there who will open the transformer while energized for routine examination.
It is all but impossible to idiot proof an installation.
What if the working clearance problem is solved, but some unqualified person opens any energized compartment, much less an MV one, anyway?
What NEC violation?True. But, If there’s an injury or death, how will a jury view it if they can prove a NEC violation was involved?