I change my answer too. We didn't get the concrete part, and I agree with what C3PO said.
I agree that wood would be a non-grounded surface. I do not agree about the sheet rock. But I have no fact to offer to support that opinion. I will say that if I needed to construct a surface that would allow me to use the Condition One distances, I would not choose sheet rock.iwire said:There is no way I would consider a wood or sheet rock wall as 'grounded'
C3PO said:Since the wall is concrete then I change my answer to condition 2 (3' 6")
I still do not consider a receptacle to be an exposed live part.