ronaldrc said:
I have redrawn this scenario with the utility grounding jumper.
http://home.comcast.net/~ronaldrc/wsb/High_voltage_illistration.htm
Chances are of this ever happening are very slim.
But never the less it could happen.
Great thread everyone. Definitely makes a person think.
Now, looking at the diagram, with the broken line side high-voltage grounded conductor, how much current would actually flow in the service drop neutral and the GEC?
Say we have a 100 amp load in the dwelling (which is probably higher than normal). So multiply this by 240 volts equals 24,000 VA.
Let's go with 34,000 volts to ground on POCO primary. The current which would travel through the primary winding and then down the service drop neutral to the GEC would be 24,000 divided by 34,000 equals .7 amps.
What about the high voltage on the neutral? Since the neutral is connected to the center of the secondary windings, and also connected to the earth through the GE, there would not be any drastic increase in the potential difference between any of the secondary service conductors, branch circuits, etc.
The only place I see a large potential difference may be between each side of where the original wire was broken on the primary side. And even that is subject to debate based on the different resistances of the dwelling GE and what is on the other side of the broken wire.
Now, considering that we don't hear about thousands of fires and thousands of electrocutions caused by this phenomenon, I don't think it is as bad as it is made out to be. Of course, I may be wrong, and there may be a huge government/media/poco conspiracy involved.
I haven't read the IEEE report cited above, but will do so shortly.