Stumbled upon this old photo, just curious what violations this constitutes. At least I am hoping it does- I can't say this should be allowed.
Can't tell from that angle, but you have single conductors going through holes in a steel box, so that's probably a violation (no slots or non-ferrous plate). There's also the question of what's on the end of those single leads and whether they're suitable for the use, whatever that is. And whether you can backfeed from a generator if one is attached.
Is that a 6-pole switch? It's hard to see where all of the conductors go.
Yes, 6 pole manual ATS.
A manual automatic transfer switch? Maybe it's just a manual transfer switch.![]()
I'm calling fake. Nobody in the real world puts phase tape on that evenly.
The blatant disregard for the proper use of a 4"sq blank plate.
Roger
I see the violation. There's no bushings on the EMT for the emergency light.![]()
If that is an emergency or legally required standby system the cord for that emergency light is too long.
3 ft. maximum length.
701.12 (G) or 700.12 (F) (2)
And it should be on the lighting circuit for that room. Really no way to tell about that....
300.3(A): "Single conductors specified in Table 310.104(A) shall only be installed where part of a recognized wiring method of Chapter 3"
Unless those conductors are single conductor flexible cord, they would need to be in a chapter 3 wiring method.
As mentioned slots need to be cut between entries into the enclosure, or non ferrous material needs to be used in the area where the single conductors enter (if single conductors are allowed).
The blatant disregard for the proper use of a 4"sq blank plate.
Roger
Then what we can see is probably ok. Whether or not flexible cord is even allowed is a possible issue, but from what we can see in the picture we don't know enough to determine if it is allowed.But what if they are flexible cord?