You would hate me, I will grind the paint to bare metal when bonding an SDS, connecting a GEC to building steel.
You don't think that it is required by 250.12?
Maybe on the larger service disconnects, but, in general most service disconnect switches already have the neutral kit installed and you simply install the green bonding screw through the hole to the enclosure which I would hope satisfies the rule.
If not, there's probably thousands of service disconnects out there that are improperly bonded. I've never removed the factory installed neutral kit from a service disconnect, ground the paint off behind it, reinstalled the neutral kit, ground the paint off of the green bonding screw and installed it. I don't think all that's necessary.
I feel the threaded bonding screw you get cuts the paint out of the hole as it threads in and catches at least 2 threads.
I feel the same way about the studs in a Nema 12 Hoffman box, which are welded to the enclosure prior to being painted. If you install a ground lug over the stud of a Hoffman box and tighten a 3/8 shoulder nut down on the top of it, I feel the contact on the underside of the nut to the face of the lug is a good electrical conection.
I do however like you, grind the primer off of a beam when I drill a hole through it and add a lug.
JAP>