You are correct. I was just thinking about that.Bonding would not have prevented the shock in the scenario he's describing.
Bonding is what caused the gutter and all the other parts to become energized.
The maintenance man became parallel with the neutral return path.
Nothing would have prevented this shock short of removing the neutral return current prior to him touching the energized parts.
JAP>
There really is no way to prevent the shock hazard from an open neutral if you are touching any part of the electrical system or conductive item that is connected to the electrical system and the "earth, other than killing the power source.