Re: Wye-Delta issues
RC,
you mentioned this "The 240 V secondary on the unfaulted phases will drop to 208 V [208= 240 x (6.9/7.96)]. But these two voltages will be in phase and will add to 416 V across the third phase. Phase-to-ground voltages depend on which transformer blew. They could be 120V, 120V, 360 V. Or, if the open fuse is on the 120/240V grounded transformer, they could be 208V, 208V, 0V.
Please note that the power legs are tied together to make 4 wire Delta. if we call the center-tapped leads L1, N, L2, and the other two transformer leads, power legs (P), are tied to make the fourth lead. then if I understand you right the secondary line voltages will be 208 between L1 & L2, and 208 between say L1 & P, and 416 between L2 & P. is that correct????
Also, the single phase voltages on the secondary must be 208/2=104 between L1 and N, and 104 between L2 and N, and 208+104=312 between P and N instead of 120,120, and 360.
Please assume the blown transformer is the non-grounded transformer and if no connection remain to the other two transformers...then the system should operate as open wye open delta, correct?