ok, finally got some progress from the poco ... and the [old thread of the same name] old thread is closed
re: transformer / secondary wire sizing for a big inrush elevator current.
quick background
Elevator soft starts - lights dim every time
156a 208v 3p pretty new elevator - soft start has been optimized. 312a instantaneous inrush
Isee 108kVA instantaneous demand for the elevator inrush alone and 200' of run
175a cb on the elevator disco with less~50' 2/0 Cu
600a service HAD [3] 50kVA TX at 200' run w1000mcm AL
poco replaced them with
3-100KVA banked TX's, they are showing about 150Kva load between them so they're 50% loaded
In total they've quadrupled the secondary size from the smallest section 1-1/0Cu to a continuous 500Cu run, including a #5 Box to accommodate that. Of course doubling the service run as well from 1-1000Al QPX to include 1-500Cu QPX. Loosely speaking they’ve doubled the size of everything. The only solution that remains is adding a TX right outside the building
I still think the xfmr is too small! But they have doubled everything and say that's it.
Report from the users is that the lights are still dimming, worse than before, but that may just be because they are sensitized to it now.
My question is:
Are those three oil filled round transformers
enough to drive 156 amp three phase elevator
load w a 312 amp inrush current...
Along with the 8 other apartment General use Meters
what about the I R drop over 200'
should this xfmr/secondary combo be able to drive the 156a elevator and keep VD below 5%?
We had 8-10%
I'm going in with a FLIR camera and heat test everything.
I suggested they come in with a 100+kVA load bank and "superbeast" it at both sides of the meter
re: transformer / secondary wire sizing for a big inrush elevator current.
quick background
Elevator soft starts - lights dim every time
156a 208v 3p pretty new elevator - soft start has been optimized. 312a instantaneous inrush
Isee 108kVA instantaneous demand for the elevator inrush alone and 200' of run
175a cb on the elevator disco with less~50' 2/0 Cu
600a service HAD [3] 50kVA TX at 200' run w1000mcm AL
poco replaced them with
3-100KVA banked TX's, they are showing about 150Kva load between them so they're 50% loaded
hope someone here is more knowledgable than me about how 3 round xfmrs at 100kva are half loaded at 150kva.
When 1 big dry 150kva 3ph transformer would be fully loaded
Separate mag fields more efficient than one combined?
In total they've quadrupled the secondary size from the smallest section 1-1/0Cu to a continuous 500Cu run, including a #5 Box to accommodate that. Of course doubling the service run as well from 1-1000Al QPX to include 1-500Cu QPX. Loosely speaking they’ve doubled the size of everything. The only solution that remains is adding a TX right outside the building
I still think the xfmr is too small! But they have doubled everything and say that's it.
Report from the users is that the lights are still dimming, worse than before, but that may just be because they are sensitized to it now.
My question is:
Are those three oil filled round transformers
enough to drive 156 amp three phase elevator
load w a 312 amp inrush current...
Along with the 8 other apartment General use Meters
what about the I R drop over 200'
should this xfmr/secondary combo be able to drive the 156a elevator and keep VD below 5%?
We had 8-10%
I'm going in with a FLIR camera and heat test everything.
I suggested they come in with a 100+kVA load bank and "superbeast" it at both sides of the meter