If the Uitlity is providing 5-wire service, 13.8 kV, 3 hots, 1 neutral and and EGC as the power source for a Y:Y transformer. 
They have insisted that our distribtion transformers be yg:yg.
The Utility service transformer will be grounded and bonded at the primary and secondary.
I think I need to run 5-wire to the primaries, and bond the neutral to the egc at each primary. It sounds wrong, since the egc and neutral are the same point.
I know if I'm running the secondary to a switchborad with no single phase loads I can get away with 4-wire, carrying the neutral to the geqar.
Is there any way to legally use 4-wire on the prinary?
Thanks for any responses.
John M
	
		
			
		
		
	
				
			They have insisted that our distribtion transformers be yg:yg.
The Utility service transformer will be grounded and bonded at the primary and secondary.
I think I need to run 5-wire to the primaries, and bond the neutral to the egc at each primary. It sounds wrong, since the egc and neutral are the same point.
I know if I'm running the secondary to a switchborad with no single phase loads I can get away with 4-wire, carrying the neutral to the geqar.
Is there any way to legally use 4-wire on the prinary?
Thanks for any responses.
John M
 
				
 
 
		 
 
		