bphgravity said:
Not true. This only applies to SINGLE rod, pipe, or plate electrodes.
Yes, but this means very little if all equipment is bonded properly.
I type slowly, so please read slowly to protract the misery like I have...
It took me so long to type, I had to log back in again!
I'm not trying to argue for argument's sake here, but I must answer the post thusly.
It's a little tough to appreciate the Code by taking a single passage out of context. The Code requires that single components of 250.52(A)(5) or 250.52(A)(6) must either be <= 25 ohms, or be augmented by using one or more of the elements in 250.52(A)(2) through 250.52(A)(7) in order to reach the 25 ohm maximum value.
Most construction uses elements in the GES from the following:
250.52(A)(1) Metal Underground Water Pipe, and
250.52(A)(5) Rod and Pipe Electrodes.
The argument you are giving about 250.56 only applying to single electrodes is flawed because you aren't citing 250.53(D)(2). Basically, the requirement for the 25 ohms is pointed at cheaper installations trying to minimize cost and time by doing the least possible work. The Code permits the single rod or pipe to augment the metal underground water pipe alone if the rod or pipe makes 25 ohms. If it doesn't, you can't bond to the water pipe again; you have to buy another rod or pipe and pound it in the ground no less than 6 feet from the first one to try to get to the 25 ohm limit. [edited to show that only *one* additional electrode must be added. Thanks to Jim Dungar for the POI.]
Although the panel doesn't come right out and say it, the expectation is that you'll meet the 25 ohm requirement with components selected from 250.52(A)(2) through 250.52(A)(4). These elements typically come into play in larger structures. These elements are not typically associated with, say, residential construction and wiring.
Equipment bonding, in your context (if I'm not mistaken), is for fault current path provisioning, and does not come into play for grounding. If everything's bonded properly, all of it will enjoy the same voltage stresses during the unmitigated lightning strike.
A five acre, 2 story metal roof manufacturing facility on a hilltop in northeastern Wisconsin doesn't benefit from grounding if its service is only 480V???
edited to korrekt speling misteaks
Dan