dsteves
- Appleton, WI
A line surge is a voltage spike (really an energy spike)
http://en.wikipedia.org/wiki/Voltage_spike
According to the Standard Handbook of Electrical Engineers, thirteenth edition, by Fink and Beaty, table 27-2, Power System Overvoltages are tabulated into three categories.
Category 1 is "Power frequency overvoltages", described as "temporary overvoltages dominated by the power frequency component", caused by electric faults, sudden load changes, or ferroresonance.
Category 2 is "Switching Overvoltages", described as "temporary overvoltages resulting from a switching operation", caused by energization of lines, de-energization of capacitor banks, fault interruption/TRV, high-speed reclosing, energization/de-energization of transformers, etc.
Category 3 is "Lightning overvoltages", described as "temporary overvoltages resulting from a lightning stroke terminating at a phase conductor, shield conductor, or any other part of a power system", caused by lightning-cloud to ground flashes.
They are listed in increasing value of per-unit overvoltage magnitude.
The author of the section, Prof. A. P. Sakis Meliopoulos of Georgia Institute of Technology, goes on to say, "Grounding plays an important role in dissipation of lightning strokes and therefore controlling overvoltages resulting from lightning. Yet, grounding has been widely misunderstood and proper analysis models are scarce." (You said it, Buster!)
If your system can deal with lightning overvoltages effectively, it will deal with lesser magnitude and higher frequency of occurrence sources also.
Dan
Dan