georgestolz said:P.S. - Nice Python quote, I didn't get it but have to show respect to the Pythons.
Maybe this'll help: http://www.minderella.com/words/cheeseshop.htm
georgestolz said:P.S. - Nice Python quote, I didn't get it but have to show respect to the Pythons.
Bob NH said:A commercial device to measure the resistance is pretty expensive, but I have done it by putting 120 Volts to the rod through a 100 watt light bulb and measuring the voltage at the rod and the current through the grounding conductor.
The voltage on the ground rod can be measured relative to the grounded conductor if it is available, or to almost any nearby ground a reasonable distance from the grounding electrode that is being tested.
A little alum (aluminum sulfate) dissolved in water and put into a little hole around the ground rod will go a long way toward meeting requirements on a marginal resistance electrode.
SAFETY NOTE: You should use a fairly long wire to the rod and avoid the rod area while making the measurement so you don't step on a "hot" point that could exist if you have a high resistance rod.
dsteves said:Then the TVSS only deals with L-N or L-L, not N-G or L-G or L-L-G or L-N-G. Dan
dsteves said:It may, however, be of some help if you consider the grounding and grounded systems to be series-parallel R-L-C circuits, where you're reducing R and increasing C with grounding electrodes.
dsteves said:I went back and checked the email. The calcs are giving 0.084 ohms just for the loop of 4/0 copper. The CEE hasn't been factored in yet, but I'm reasonably sure the parallel combination should get us to < .050 ohms.Dan
haskindm said:I had an engineer tell me one time, that the reason they specified an extremely low resitance grounding system and ground ring around the building was for SECURITY, not electrical safety. The theory was that an extremely good ground would eliminate the signals put out by computers and prevent unauthorized people from capturing this data. I don't know if this is a valid theory, but that is the reason that was given.
tallgirl said:they'd have to enclose the entire building, including windows and doors, for that to work.
jtester said:I just finished one of those kinds of buildings, and the approach was called TEMPEST shielding, which was an older government approach to limiting the effects of neuclear blasts on computers, etc. It has since evolved into shielding to avoid snooping.
Jim T
iwire said:We are doing an office for a Govt agency with a 3 letter name.
don_resqcapt19 said:Julie,
In most respects the EMP harding provides more shielding than what is required for TEMPEST...in other words it will do both jobs. 9-3(b) in this document, says that TEMPEST requires 50dB and EMP requires 100dB shielding. According to the online documents that I have found, the shielding works in both directions...it keeps stuff in(TEMPEST) as well as keeping stuff out(HEMP).
Don
That is a point that I didn't think about.Remember that it isn't always keeping stuff away from outside-the-building people, but it can also be keeping stuff in the room which is inside the same building as the rest of the rooms.