I see seven yes votes (Two from inspectors who might be "requiring" this) and zero arguments as to why a yes vote is the correct vote. 
I see seven yes votes (Two from inspectors who might be "requiring" this) and zero arguments as to why a yes vote is the correct vote.![]()
I see seven yes votes (Two from inspectors who might be "requiring" this) and zero arguments as to why a yes vote is the correct vote.![]()
people who voted yes are clearly outnumbered and wrong.![]()
And you are probably right. Could you explain it then? What language shows that we clearly do not have a separate space?
Possibly some of those that voted 'Yes' haven't looked it up. Charlie's Rule in action!
I didn't bother to look it up. I voted based on the code articles that were posted by George. In the diagram there is 12.5 inches behind the sink, therefore it doesn't divide it into 2 countertops, which then means that the recept. that is already there suffices.![]()
no. It would be different but right.So suppose George (no offense intended here, George!) mistyped and put 11?" instead of 12?"? Your answer would be different, but wrong.
No typo. But I am curious about the "yes" votes.So suppose George (no offense intended here, George!) mistyped and put 11?" instead of 12?"? Your answer would be different, but wrong.
If countertop spaces are separated (by a sink), each section would be considered as separate spaces in applying 210.52(C)(3).
Reading the actual text of 210.52(C), an area behind the unit (sink) with a width of less than 12 inches qualifies as separating the countertop.
Now CMP 2 probably meant depth, and that word would make it ok.
I will agree that it should'nt be required, was not likely meant that way, but that is what it says according to standard dimensional language.
So suppose George (no offense intended here, George!) mistyped and put 11?" instead of 12?"? Your answer would be different, but wrong.
<12" triggers 210:52(C) paragraph 2 that the left and right of the sink are separate peninsula areas. Therefore 210:52(C)(3) kicks in. Then it becomes Yes.
you are wrong. Re-read it and re-read it and re-read it again until you understand that in George's diagram the counterspace is 12.5" which as 480 said is larger than 12" which in turn means that the counterspace is not divided in 2 by the sink. This therefore means that the one recept. already in place suffices.<12" triggers 210:52(C) paragraph 2 that the left and right of the sink are separate peninsula areas. Therefore 210:52(C)(3) kicks in. Then it becomes Yes.