Yuck

Status
Not open for further replies.

vasparky27

Member
Location
Chesapeake, Va.
Friend wants a favor......
House is being sold, looking forward to hearing from the home inspection company.
c99b8d22c2061efe0dbc07c2824cf0d8.jpg
79195b0063e2a34ed31eb19f0e3d0f74.jpg
e69598f71f2893e5ab4629a03eaa94e6.jpg


Sent from my SM-G892A using Tapatalk
 
Last edited:
Not bad. Get a new 60A subpanel, properly grounded, replace the box with the missing side, install GFCI receptacle, eliminate the empty conduit in the bottom (or put a lockring on the fitting), staple down the NM within a foot of the panel and every 3' after, done. Hundred bucks in material and two hours labor to fix what's pictured.

eta: please dont tell me the 3/4" plumbing PVC 90's into that panel as the feeder....
 
Last edited:
Not bad. Get a new 60A subpanel, properly grounded, replace the box with the missing side, install GFCI receptacle, eliminate the empty conduit in the bottom (or put a lockring on the fitting), staple down the NM within a foot of the panel and every 3' after, done. Hundred bucks in material and two hours labor to fix what's pictured.

eta: please dont tell me the 3/4" plumbing PVC 90's into that panel as the feeder....

I think you have seen the future all too clearly.:happyyes:
 
Not bad. Get a new 60A subpanel, properly grounded, replace the box with the missing side, install GFCI receptacle, eliminate the empty conduit in the bottom (or put a lockring on the fitting), staple down the NM within a foot of the panel and every 3' after, done. Hundred bucks in material and two hours labor to fix what's pictured.
.

Sounds good, when can u start ? :D
 
...
eta: please dont tell me the 3/4" plumbing PVC 90's into that panel as the feeder....
Actually, it looks like plumbing PVC pipe, but the fitting going into the panel looks like a larger BX 90 degree connector clamped down onto it! A hack of a hack! :slaphead:

Those old Sears panels were brand-labeled Murray. Current Siemens / Murray breakers and fillers still work and are listed for use with them.
 
Vans out of the shop. Off to work I go.
The homeowner sent a list of things that need too be done at this location.
Rolling...

Sent from my SM-G892A using Tapatalk
 
Yes its plumbing pipe with THHN inside. 2 HOTS AND A GROUND WIRE
going back out today to look at other issues.


Sent from my SM-G892A using Tapatalk

OK, I see what look like two runs of NM going out the top. Lemme guess; one hot per and the grounds are tied together? Or is it two 240 volt loads?
 