Summarizing,
The Part 1 calc, illustrated that the voltage-triangle of an unbalanced Y-connected load supplied from a 3-ph, 4-wire, source, will remain intact!
The Part 2 calc, illustrated that the voltage-triangle of an unbalanced Y-connected load supplied from a 3-ph, 3-wire, source, will became distorted, and its neutral-point displaced or shifted!
And now Part 3!
How does an isolated-neutral affect performance of a Y-Y transformer? For simplification purposes I will ignore harmonic effects!
First consider insulation! Typically, if wye-connected, and neutral-grounded, then insulation (between core and coil) is usually reduced for economic reasons! But, if the neutral is isolated, then full-voltage insulation is required!
Secondly, and more importantly, is the imbalance of excitation-current for each of the three primary-windings connected to the source! When the 3-winding mid-point is connected to source-neutral, therir excitation-currents, Iea, Ieb, Iec, magnitudes are (almost*) equal, and their sum (almost*) zero! But when their mid-point is isolated, their Ie parameters are unequal, so that, for example, Iea = Ieb + Iec, failure is certain!
Note:
The (almost*) term represents the fact that Ie magnitude is dependent on the circuit-model used! If Ie components are located at the Xfmr?s primary-winding terminals, the so-called ?Pi? model, then Ie is affected by only source-voltage! But, if Ie components are located after the primary winding-impedance, the so-called ?T? model, then Ie is affected by both source-voltage and load-current!
Regards, Phil Corso