Hello all. I need a slight dirrection towards bonding and grounding a 100 amp. eter socket combination main disconnect. Local ahj wants ground rod and gec to water meter. What i plan to do is:
-bond neutral at main disconnect (meter socket),
-run a gec to ground rod from meter socket.
-run my 3- service conductors in pipe 15 feet away to breaker panel
- and since an additional supplemental ground is needed, i plan to run a conductor from ground buss bar to water meter...
Does this sound right according to N.E.C? I don't want to take any short cuts. Another inspector passed one of my jobs like this recently but i'm a little skeprical about his knowledge as well...
Thanks all!