Ouch! I'm glad I live in the land of hydro-electric power. I like my $80/month electric bill.
What do you pay per kw ?
Ouch! I'm glad I live in the land of hydro-electric power. I like my $80/month electric bill.
Your turkey would be burned to a crisp if the oven element remained on for the whole duration.most every thanksgiving my oven runs for well over 3 hrs. how can it not be a continuous load ?
Ultimately, it does not appear as though all four burners and the elements would be on at the same time for 3 hours therefore it is unlikely that a range would be considered continuous for normal use. Heating the house (for which it is not designed or listed) does not count.
With that being said, a 40A circuit would be the code minimum circuit.
I know that many EC's would put in a 50A circuit just to play it safe and give the homeowner more options if they replace the unit in the future.
It also looks as though the 40A circuit crowd is the majority although this is not a blowout which shows how differently we are.
Personally, I automatically put in at least a 50A circuit unless it needs to be bigger. The code says 40 but that of course is the minimum allowed thanks to the derating of the NEC table.
You are making a good point.
We have been referencing 220.55 which is for feeder and service load calculations, not branch circuit ratings.
If we tip toe back to 210.19 dealing with branch circuit ratings, it clearly states that the conductors shall not have a rating less than the load to be served. It further states that ranges 8.75kW or more must have a minimum of a 40A branch circuit.
So when sizing the branch circuit, do we strictly go off of the data plate?
If we are suppose to derate the branch circuit in Table 220.55, don't you think we would be directed to do so in the 210 section?
What about note #4 to table 220.55?
What about note #4 to table 220.55?
Does anyone have an issue with putting a 50-amp receptacle on a 40-amp circuit?
Does anyone have an issue with putting a 50-amp receptacle on a 40-amp circuit?
210.21(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit
I still see that as a service load calculation issue. Not a branch circuit sizing table.
40 amp circuit.
- As per 220.55, using the Table 220.55, column C.
- 12.5kW is a "major fraction thereof" (note 1)
the demand load is 8kW
8000W x 1.05 = 8400W/240V = 35Amps
I agree with Pierre this is how I would do it ,...the major fraction is treated as 1kw.
I would install an 8/3 with a ground. Install a 4 wire 50 amp recep and a 4 wire 50 amp pigtail. Since it is a 50 amp circuit rated for 50 amps, I would place a 50 amp breaker for the overcurent device.
That would be a violation, 8/3 NM and now 8/3 SE are both rated 40 amps, you can not use a 50 amp breaker.
I swear I have not seen you in this post until I replied. I understand what you are saying. Keep in mind, I am using the 2002 code and I am waiting until we adopt 2008. I have kept telling my boss about what I have read here but it does not seem to phase him. My boss is 80 yrs old.
As far as I am concerned, our local AHJ have allowed us to wire electrical but at the same time they have allowed us to do so that violates code. Example would be using romex in conduit.
I have argued quite a bit with my boss to get a fire under our local AHJ's rears. I dont like it that we adopt a part of a code book and I dont like it that I cannot obtain a full version of the county codes.
I want it to where I have a book I can go by to do my thing,, but no, I can only rely half way on my book and can only learn anything when I get turned down.