M. D. said:
I didn't think so,.. but what about the words " all fixed metal parts ",..why stop with the examples the author lists ??...or would I be required to bond the letter slot and door bell button too... how do you stop giving examples of "all fixed metal parts,... when there are none left to bond??
Do throw in the "likely to be energized" phrase after parts ?
Metal fittings that are part of the pool are not required to be bonded if they are 4" or smaller and do not penetrate into the structure more than 1" , but " all metal parts " within 5' of the the inside edge shall be bonded
"why stop with the examples the author lists ??"
I wouldn't, I don't.
"how do you stop giving examples of "all fixed metal parts,... when there are none left to bond??"
yes
"Do throw in the "likely to be energized" phrase after parts ?"
Someone could copy some sentence structure from 250.104 and put in a proposal to add it into 680.26, but as of now, it isn't there and the '08 edition of 680.26(B)(5) went in a different direction. . I think 680.26(B)(5) is more applicable than 250.104 in this situation.
"would I be required to bond the letter slot and door bell button too"
Here's where I go for window or door frame:
#1] What does the wording in the NEC actually say ? . Is it clear ? . If yes, then skip to #4.
The word "parts" is not clear, I'm going to step #2.
#2] Is there other language within the NEC that might not directly apply but can help understand a word or phrase ? . If yes, then skip to #4.
I'm looking at stuff like 250.104 + 680.26(B)(5) and there's no clear help to be found, I'm going to step #3.
#3] Is there info in an ROP, NEC Handbook, or UL Whitebook that helps clear up the question ?
Yes, the Handbook is clear.
#4] Take the best answer you have at this point and apply common sense to the specific installation that you're looking at.
Common sense tells me that you can get shocked from a metal frame that's within 5' of the pool.
#5] Is it still unclear which of several options are required ? . Then accept any of those possible options that the contractor chooses.
The Handbook is clear, that will be the finding of my inspection.
Here's where I go for door bell button:
#1] What does the wording in the NEC actually say ? . Is it clear ? . If yes, then skip to #4.
Not clear, I'm going to step #2.
#2] Is there other language within the NEC that might not directly apply but can help understand a word or phrase ? . If yes, then skip to #4.
680.26(B)(5) is helpful when looking at stuff that's has a long dimension not over 4". . If a metal fitting attached to the pool isn't required to be bonded, now I'm looking at a metal doorbell button that's removed from the pool by 5' or less. . I'll look at this concept again in step #4, I'm going to step #3.
#3] Is there info in an ROP, NEC Handbook, or UL Whitebook that helps clear up the question ?
No, everything in the Handbook is considerably bigger than a door bell button.
#4] Take the best answer you have at this point and apply common sense to the specific installation that you're looking at.
I go back to the 4" spec in 680.26(B)(5). . That makes sense to me.
#5] Is it still unclear which of several options are required ? . Then accept any of those possible options that the contractor chooses.
I would not require the door bell button to be bonded according to where I'm at after step #4.
Here's where I go for letter slot:
#1] What does the wording in the NEC actually say ? . Is it clear ? . If yes, then skip to #4.
Not clear, I'm going to step #2.
#2] Is there other language within the NEC that might not directly apply but can help understand a word or phrase ? . If yes, then skip to #4.
680.26(B)(5) is helpful when looking at stuff that's has a long dimension not over 4" but I've never seen a letter slot that wasn't longer than 4". . Not clear, I'm going to step #3.
#3] Is there info in an ROP, NEC Handbook, or UL Whitebook that helps clear up the question ?
No, the Handbook doesn't discuss the letter slot of anything similar.
#4] Take the best answer you have at this point and apply common sense to the specific installation that you're looking at.
You wouldn't have the exposure of damaging a cord in the letter slot, nothing like the exposure that a window or door frame has.
#5] Is it still unclear which of several options are required ? . Then accept any of those possible options that the contractor chooses.
Still unclear. . I would accept the contractors option and I would tell him that his installation is not clearly code compliant and that fact might have an increased liability for him. . His choice.