E.M.T. good for ground

Status
Not open for further replies.

lendog

Member
Location
California
Hi does anybody know were in the code book it says how many amps e.m.t. is good for ground. Someboddy asked me where in the book it says it, but I cant find it.
 

iwire

Moderator
Staff member
Location
Massachusetts
lendog said:
Hi does anybody know were in the code book it says how many amps e.m.t. is good for ground. Someboddy asked me where in the book it says it, but I cant find it.

Nowhere in the NEC is it limited by amps.

EMT is allowed as an EGC per 250.118.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
iwire said:
Of course not, it will never work. :grin:

No Bob i did not say that.It might and then again it just might not.All we need is 1 set screw that wasnt tightened or conduit that got hit and came apart.Then we have something worse than no ground at all.
 

iwire

Moderator
Staff member
Location
Massachusetts
Jim W in Tampa said:
All we need is 1 set screw that wasnt tightened or conduit that got hit and came apart.Then we have something worse than no ground at all.

All we need is 1 wire-nut that wasn't tightened or wago that got hit and came apart.Then we have something worse than no ground at all.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
iwire said:
All we need is 1 wire-nut that wasn't tightened or wago that got hit and came apart.Then we have something worse than no ground at all.

Ahhhh but in Jim's case you still have the EMT for the ground.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Jim, consider this, a properly installed metallic conduit recognized in 250.118 is a better EGC than a properly installed insulated conductor.

What is the common denominator in that statement?

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Dennis Alwon said:
Ahhhh but in Jim's case you still have the EMT for the ground.

But if the same installer did both, how would you guarantee either ones quality?

Roger
 

peter d

Senior Member
Location
New England
As I said the last time this issue came up, we always splice with 100% accuracy but we somehow forget to make sure our raceways are mechanically sound. ;)
 

iwire

Moderator
Staff member
Location
Massachusetts
Dennis Alwon said:
Ahhhh but in Jim's case you still have the EMT for the ground.

I was taking NM jobs, are your suggesting we should always run redundant grounds? :grin:

By the way, run an EGC, don't run an EGC I really don't care. :)

Sometimes I do, sometimes I do not, depends on many things. :smile:

What I try to do is get people to think about the reasons why they do the things they do.

Don't just do things because you have always done them, or that was 'how I was taught', or someone said it was better, ask yourself why. :cool:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
roger said:
But if the same installer did both, how would you guarantee either ones quality?

Roger

That's why you bring in a third party and pull another ground wire just to be safe. :grin:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
peter d said:
As I said the last time this issue came up, we always splice with 100% accuracy but we somehow forget to make sure our raceways are mechanically sound. ;)

But Peter, if the conduit is not mechanically sound, what's protecting the EGC inside of it? ;)

Roger
 

iwire

Moderator
Staff member
Location
Massachusetts
Dennis Alwon said:
That's why you bring in a third party and pull another ground wire just to be safe. :grin:

:grin:

Can we also require tests, send emails and have meetings about the grounding for each circuit? :D
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Dennis Alwon said:
That's why you bring in a third party and pull another ground wire just to be safe. :grin:

This reminds me of security when working inside a Casino.
They send a guard to watch you and another guard to watch him and all the while all of you are being watched on camera.:)

Roger
 