Before y'all jump in and say that this has been beat to death, look what I found in the install manual of the new 6247 (14KW NG/LP standby Gen). It's a non-SDS.
This seems to be new wording over what I've read about in the past. It requires a grounding and grounded conductor run from the house (where they're bonded)
so I'd say that its connected to approved earth ground without the rod.
Has Generac finally gotten this right?
Generac 6247 Installation Guidelines said:The National Electrical Code (NEC) requires the frame and external electrically conductive parts of the generator to be connected to an approved
earth ground. Local electrical codes also may require proper grounding of the generator electrical system.
This seems to be new wording over what I've read about in the past. It requires a grounding and grounded conductor run from the house (where they're bonded)
so I'd say that its connected to approved earth ground without the rod.
Has Generac finally gotten this right?