is it permissable to install a 120v /20amp duplex receptacle above a suspended ceiling. this outlet would serve a plug in power supply for a CCTV camera/
mfbettwy said:is it permissable to install a 120v /20amp duplex receptacle above a suspended ceiling. this outlet would serve a plug in power supply for a CCTV camera/
MAK said:I ran into something similar with a camera installation at a school. The head of maintenance directed us to mount equipment above a drop tile ceiling and he would have his electrician install an outlet above the ceiling for us to connect our power supply and line cord for an LCD monitor. I had mentioned to him that I did not think that you could mount the equipment above the drop tile but had no idea what the code reference would have been.:-? If it were just a plugin transformer (class 2 24vac 40va) would there be a problem with that?
Energize said:Not sure where they are getting the information that only rubber cords are not permitted. I see nothing to indicate the compound of the insulation dictates compliance. It just states "flexible cords and cables".
400.7 Uses Permitted
(A) Uses Flexible cords and cables shall be used only for the following:
(6)Connection of utilization equipment to facilitate frequent interchange
(8)Appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection
400.8 Uses Not Permitted
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(5)Where concealed by walls, floors, or ceilings or located above
suspended or dropped ceilings
volt102 said:Even if it is rubber cord.
Since frequent interchange in specifically permitted by 400.7, especially considering that many security cameras are moved around all the time so no one can figure out which ones are the dummies. I understand that this may not apply to the OP, as it has many variables. I just wanted to point the fact that we may install a receptacle above a ceiling and plug something in it....
The same can be true for installing the condensate pump next to an air handler unit. A Receptacle installed above a drop ceiling and a cord and plug "Little Green Giant" may all be installed above the suspended ceiling, because it is also on the permitted list specifically permitted by 400.7(8) for maintenance...
volt102 said:A Receptacle installed above a drop ceiling and a cord and plug "Little Green Giant" may all be installed above the suspended ceiling, because it is also on the permitted list specifically permitted by 400.7(8) for maintenance...
400.7(A)(6) does not, IMO, allow you to install a flexible cord above a suspended ceiling.
appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection
jim dungar said:From what I have read in this forum, the basic argument is:
400.7 does not specifically allow any of the items to be above a suspended ceiling?
jim dungar said:From what I have read in this forum, the basic argument is:
400.7 does not specifically allow any of the items to be above a suspended ceiling?
400.7 Uses Permitted
(A) Uses Flexible cords and cables shall be used only for the following:
(6)Connection of utilization equipment to facilitate frequent interchange
(8)Appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection